Most grid tie inverters nowadays are transformerless, so you absolutely
cannot reference the DC input to ground in any way.   It will end in smoke
and/or tears!

On Sun, Mar 21, 2021 at 9:43 AM Robert Bruninga via EV <ev@lists.evdl.org>
wrote:

> Sometimes in the field I have run over 3000 feet of #22 hookup wire to run
> several hundred watts from my car for ham-radio camping using
> ground-return.
> See: APRS SWER Power Distribution <http://aprs.org/aprs-swer.html>
>
> If your solar is a series string array, then the voltage is approaching 500
> volts.  The loss is I squared R so the loss at 500v is less than a 4th of
> what it is at 240v.
> Lets try #12 wire has a resistance of 5 ohms over 2000 feet, so the loss
> from say a 10 kW array (20 amps) is 2000W or a 4th of your power, but if
> you get to the 6 cent meter you get double the value so it is a net gain of
> 2.  But that is 1 wire. If you used a perfect ground for the return.
>
> THe ground return might be a best case 10 ohms, but then that is in the
> wilderness.  If both systems are near utilities which are firmly
> grounded then most of the current might flow through the low resistance
> utility grounds (but making an unsafe condition on loss of grounds).
>
> Just thinking...
>
> One other problem is that most string grid-tie inverters do not like to see
> any ground current and will trip (though this can be spoofed).
>
> Bob
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.evdl.org/private.cgi/ev-evdl.org/attachments/20210321/50187d31/attachment.html>
_______________________________________________
Address messages to ev@lists.evdl.org
No other addresses in TO and CC fields
UNSUBSCRIBE: http://www.evdl.org/help/index.html#usub
ARCHIVE: http://www.evdl.org/archive/
LIST INFO: http://lists.evdl.org/listinfo.cgi/ev-evdl.org

Reply via email to