There are also minor differences if the product is installed in a gas-insulated 
substation, air-insulated substation, or a power station within 61000-6-5.

There is a fair amount of EMC standards that might be applicable to a device 
within a substation depending on the location of installation and function. If 
the product has a protection function, then the 60255-1, 26 might be applicable 
while protection communications might need 61850-3.

Bill

From: Charlie Blackham <[email protected]>
Sent: Wednesday, April 17, 2024 9:45 AM
To: [email protected]
Subject: Re: [PSES] IEC 61000-6-5 vs. IEC 61000-6-2

[Caution - External]
Amund

There are a number of differences including:

  *   Zoning of different areas which then require different levels of tests 
against 61000-4-4; 61000-4-16 and 61000-4-18
  *   61000-4-8 Mag Field is 100 A/m continuous and 1000 A/m for 1 s (but only 
for equipment containing magnetically sensitive components)


You can read more for a few Euro at https://www.evs.ee/en/evs-en-61000-6-5-2015 
[evs.ee]<https://urldefense.com/v3/__https:/www.evs.ee/en/evs-en-61000-6-5-2015__;!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0JyUQOuq$>

Best regards
Charlie

Charlie Blackham
Sulis Consultants Ltd
Tel: +44 (0)7946 624317
Web: https://sulisconsultants.com/ 
[sulisconsultants.com]<https://urldefense.com/v3/__https:/sulisconsultants.com/__;!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0EkzaMry$>
Registered in England and Wales, number 05466247

From: Amund Westin <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 17, 2024 5:34 PM
To: [email protected]<mailto:[email protected]>
Subject: [PSES] IEC 61000-6-5 vs. IEC 61000-6-2


IEC EN 61000-6-2, Electromagnetic compatibility (EMC) - Part 6-2: Generic 
standards - Immunity for industrial environments

IEC EN 61000-6-5, Electromagnetic compatibility (EMC) - Part 6-5: Generic 
standards - Immunity for equipment used in power station and substation 
environment





I'm quite familiar with IEC EN 61000-6-2 but have never tested or looked into 
IEC EN 61000-6-5.

If anyone who have knowledge about both standards and could shorty tell the 
main differences between these two?





Best regards

Amund





________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]<mailto:[email protected]>
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/ 
[mail-archive.com]<https://urldefense.com/v3/__https:/www.mail-archive.com/[email protected]/*20__;JQ!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0J9Difws$>

Website: https://ewh.ieee.org/soc/pses/ 
[ewh.ieee.org]<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/__;!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0P2YKno7$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) 
[ewh.ieee.org]<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/list.html__;!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0FDmY39j$>
List rules: https://ewh.ieee.org/soc/pses/listrules.html 
[ewh.ieee.org]<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/listrules.html__;!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0BGxNuY2$>

For help, send mail to the list administrators:
Mike Sherman at: [email protected]<mailto:[email protected]>
Rick Linford at: [email protected]<mailto:[email protected]>

For policy questions, send mail to:
Jim Bacher at: [email protected]<mailto:[email protected]>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1 
[listserv.ieee.org]<https://urldefense.com/v3/__https:/listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0KwSKOp2$>

________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]<mailto:[email protected]>
All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/ 
[mail-archive.com]<https://urldefense.com/v3/__https:/www.mail-archive.com/[email protected]/__;!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0GEeHbge$>

Website: https://ewh.ieee.org/soc/pses/ 
[ewh.ieee.org]<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/__;!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0P2YKno7$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe) 
[ewh.ieee.org]<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/list.html__;!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0FDmY39j$>
List rules: https://ewh.ieee.org/soc/pses/listrules.html 
[ewh.ieee.org]<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/listrules.html__;!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0BGxNuY2$>

For help, send mail to the list administrators:
Mike Sherman at: [email protected]<mailto:[email protected]>
Rick Linford at: [email protected]<mailto:[email protected]>

For policy questions, send mail to:
Jim Bacher at: [email protected]<mailto:[email protected]>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1 
[listserv.ieee.org]<https://urldefense.com/v3/__https:/listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!O7uE89YCNVw!L49CWc_XsROMFU46RujMT5dm7yipGR1XPTc22jhXMMyJcjYVbmPUyjvdmigcR-RDjJAoRQ3ICLRJrVeD0KwSKOp2$>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to