Hi Lauren,

 

MCCB (molded case circuit breakers) get hot when they are run close to their
handle rating, even open bench.  If installed in a panel (dead air space) at
40C ambient temperature, I would expect they would easily exceed 50C on
their molded case long before say 3 hours have expired (continuous current
as defined in NFPA 70).  Their terminals are rated for 60C wire,  so those
terminals (the internal parts connected to them) can get at least that hot.
If simply heat-soaked at zero current at 50C, I'd say you have no worries.

 

It is always wise to write to the manufacturer of the circuit breaker and
ask them if they can check the "conditions of acceptability" which normally
accompanies any UL recognition.  Include ALL your test conditions in your
correspondence.

 

 

From: Lauren Crane <[email protected]> 
Sent: Friday, January 5, 2024 4:48 PM
To: [email protected]
Subject: [PSES] Is certification 'voided' by improper operational
conditions?

 

Hello Experts, 

 

If I have UL certified component and operate it for a period of time outside
its specified conditions of operation, and then return the conditions to
specified levels, is it appropriate to still think of the component as
certified, or is the certification somehow voided by this accident? 

 

For example, a circuit breaker rated for 40degC max ambient run at 50degC
ambient for 8 hours and then ambient temp brought down to 30degC.  

 

Best Regards, 

-Lauren

 

Happy to receive recall-opinions and educated guesses but would love
'chapter and verse' citations if available.


LAM RESEARCH CONFIDENTIALITY NOTICE: This e-mail transmission, and any
documents, files, or previous e-mail messages attached to it, (collectively,
"E-mail Transmission") may be subject to one or more of the following based
on the associated sensitivity level: E-mail Transmission (i) contains
confidential information, (ii) is prohibited from distribution outside of
Lam, and/or (iii) is intended solely for and restricted to the specified
recipient(s). If you are not the intended recipient, or a person responsible
for delivering it to the intended recipient, you are hereby notified that
any disclosure, copying, distribution or use of any of the information
contained in or attached to this message is STRICTLY PROHIBITED. If you have
received this transmission in error, please immediately notify the sender
and destroy the original transmission and its attachments without reading
them or saving them to disk. Thank you.

 

Confidential - Limited Access and Use

  _____  

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to All
emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/[email protected]/
<https://www.mail-archive.com/[email protected]/%20>  

Website: https://ewh.ieee.org/soc/pses/  <https://ewh.ieee.org/soc/pses/> 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
unsubscribe) <https://ewh.ieee.org/soc/pses/list.html> 
List rules: https://ewh.ieee.org/soc/pses/listrules.html 

For help, send mail to the list administrators:
Mike Sherman at: [email protected] <mailto:[email protected]> 
Rick Linford at: [email protected] <mailto:[email protected]>  

For policy questions, send mail to:
Jim Bacher at: [email protected] <mailto:[email protected]>  

  _____  

To unsubscribe from the EMC-PSTC list, click the following link:
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC
<https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1> &A=1 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to