Hi Amund:

 

In 60950-1 (and I believe similarly in 62368-1), there is no specific
requirement to have two layers of insulation.  A single layer is okay to use
if it meets the performance requirements of so-called "double insulation."
The term "reinforced insulation" is used in 60950-1 to refer to this
distinction.

 

I'm short on time today, but I'll try to elaborate further later.

 

 

Joe Randolph

Telecom Design Consultant

Randolph Telecom, Inc.

781-721-2848 (USA)

 <mailto:[email protected]> [email protected]

 <http://www.randolph-telecom.com> http://www.randolph-telecom.com

 

From: Amund Westin [mailto:[email protected]] 
Sent: Thursday, February 24, 2022 1:27 PM
To: [email protected]
Subject: [PSES] SV: [PSES] SV: [PSES] Numbers of insulation layers in
transformer (IEC62368)

 

A Class II or double insulated electrical appliance (bear the double
insulation symbol), is it required to have a transformer with 2 insulating
layers? Or is one layer in transformer ok,  if the plastic enclosure is
giving enough insulation, thus in total you will have 2 layers of
insulation?

Ref. 62368-1 product (AC powered WiFi HUB). No cabling/wiring on secondary
side.

 

Cheers!

 

BR

Amund

 

 

 

 

 

Fra: Joe Randolph 
Sendt: 18. februar 2022 05:09
Til: [email protected] <mailto:[email protected]> 
Emne: Re: [PSES] SV: [PSES] Numbers of insulation layers in transformer
(IEC62368)

 

Hi Amund:

 

In general, a safety lab does not spend time thinking about hypothetical
scenarios.  They usually focus on simply complying with the requirements of
the applicable safety standard, which in this case is 62368-1.

 

I'm still relatively new at using 62368-1, but I have lots of experience
using 60950-1.  While there are differences in how the two standards
approach the issue of safety for 230 Vac mains, I think the underlying
philosophy is the same:

 

1)      230 Vac mains should not be "accessible" to ordinary users

2)      230 Vac mains should not become "accessible" without a double-fault
condition

 

There are lots of ways to meet these criteria.  Key to both of the above
criteria is the definition of "accessible."  The method for making sure that
a 230 Vac circuit is not accessible is to carefully apply the definition of
"accessible" in the standard.  Safety standards typically define
"accessible" with various criteria including various specialized probes that
simulate a human finger, along with various criteria regarding anticipated
use.

 

I'm not sure how 62368-1 defines accessibility, but in 60950-1, a 230 Vac
circuit is considered to be accessible if it can be touched by the specified
probes without the use of a "tool" (such as a screwdriver).  Further, even
if a "tool" is required to be able to touch a 230 Vac circuit, that circuit
is considered to be accessible if the user is instructed to use a tool to
access the area, such as a battery compartment.

 

I don't know the details of the removable part on the product in question,
but perhaps the above considerations will help you evaluate the available
options.

 

 

Joe Randolph

Telecom Design Consultant

Randolph Telecom, Inc.

781-721-2848 (USA)

[email protected] <mailto:[email protected]> 

http://www.randolph-telecom.com <http://www.randolph-telecom.com/> 

 

From: Amund Westin [mailto:[email protected]] 
Sent: Thursday, February 17, 2022 2:57 AM
To: [email protected] <mailto:[email protected]> 
Subject: [PSES] SV: [PSES] Numbers of insulation layers in transformer
(IEC62368)

 

Thanks, guys!

 

I have not received a fully explanation from the safety lab, but I assume
they are concerned about this:

-          With only one insulation layer between Prim/Sec winding in the
transformer, a fault in the insulation tape will result in 230VAC in the
secondary circuits. OK, but there are no cable interfaces on the secondary
side and no conductive parts. The entire enclosure is flame category V-1 or
V-0.

But one part of the enclosure is a little piece that is pressed onto the
main part of the enclosure. This little part can be demounted, and since the
product is plugged into a 230VAC socket that is located 20 cm above the
floor, a child could manage to remove this little part and access the
secondary circuit (now 230VAC) by its fingers.

 

I guess this is the reason for requiring two layers in the transformer.

 

Or make it impossible to remove this part which can give access to secondary
circuits.

 

Best regards 

Amund

 

 

 

 

Fra: Richard Nute 
Sendt: 16. februar 2022 23:09
Til: 'Amund Westin' <[email protected]
<mailto:[email protected]> >; [email protected]
<mailto:[email protected]> 
Emne: RE: [PSES] Numbers of insulation layers in transformer (IEC62368)

 

 

 

Hi Amund:

 

Since the unit does not have grounding/earthing, it is therefore
double-insulated with respect to the input 230 volts (and must bear the
double-insulated symbol).  

 

This requires all accessible conductive parts and accessible surfaces to be
double-insulated from the 230 volts.  

 

If the secondary circuit has any accessible conductive parts (e.g., metal
antenna), then the secondary must be double-insulated from the 230 volts:
transformer must have two insulation layers, basic and supplementary. (This
is the most common construction.) 

 

If the secondary has no accessible conductive parts, then the insulation
between the secondary and accessible surfaces (whether or not conductive) is
"supplementary insulation":  transformer can have one insulation layer,
basic.  (This is uncommon construction and will likely be not acceptable to
many certification houses.)  

 

Good luck, and best regards,

Rich

 

 

From: Amund Westin <[email protected]
<mailto:[email protected]> > 
Sent: Wednesday, February 16, 2022 1:02 PM
To: [email protected] <mailto:[email protected]> 
Subject: [PSES] Numbers of insulation layers in transformer (IEC62368)

 

Do I need one or two insulation layers (tape) between the primary and
secondary windings?

Can find an absolute answer in the standard IEC62368.

 

 

Product:

Input 230VAC

Secondary 24VDC for other Low volt circuits 

No grounding /earthing

No cable outputs

Plastic enclosure

Radio HUB product 

 

Thanks.

 

Best regards

Amund

 

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected] <mailto:[email protected]> >

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected] <mailto:[email protected]> >
Mike Cantwell <[email protected] <mailto:[email protected]> > 

For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]> >
David Heald <[email protected] <mailto:[email protected]> > 

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected] <mailto:[email protected]> >

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected] <mailto:[email protected]> >
Mike Cantwell <[email protected] <mailto:[email protected]> > 

For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]> >
David Heald <[email protected] <mailto:[email protected]> > 

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected] <mailto:[email protected]> >

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe) <http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected] <mailto:[email protected]> >
Mike Cantwell <[email protected] <mailto:[email protected]> > 

For policy questions, send mail to:
Jim Bacher <[email protected] <mailto:[email protected]> >
David Heald <[email protected] <mailto:[email protected]> > 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to