Ivan,

Using an additional enum on public API for resetting dynamic value looks a
little bit dirty for me.
I'm not sure there is a problem at all, because user can always query the
current policy, and a javadoc can describe such behavior clearly.
If you really insist maybe use null to reset policy value:

ignite.cluster().setShutdownPolicy(null); // Clear dynamic value and switch
to statically configured.

On top of this, we already have a bunch of over properties, which are set
statically and can be changed dynamically later,  for example [1]
I think all such properties should behave the same way as shutdown policy
and we need a ticket for this.
In such a case we probably should go with something like

ignite.cluster().resetDynamicProperValuey(propName); // Resets a property
to statically configured default value.

Right now I would prefer for shutdown policy behave as other dynamic
properties to make things consistent and fix them all later to be
resettable to static configuration value.

[1] org.apache.ignite.IgniteCluster#setTxTimeoutOnPartitionMapExchange(timeout)



вт, 9 июн. 2020 г. в 15:12, Ivan Rakov <ivan.glu...@gmail.com>:

> Something went wrong with gmail formatting. Resending my reply.
>
> Alex,
>
> Also shutdown policy must be always consistent on the grid or unintentional
> > data loss is possible if two nodes are stopping simultaneously with
> > different policies.
>
>  Totally agree.
>
> Let's use shutdownPolicy=DEFAULT|GRACEFUL, as was proposed by me earlier.
>
>  I'm ok with GRACEFUL instead of WAIT_FOR_BACKUPS.
>
> 5. Let's keep a static property for simplifying setting of initial
> > behavior.
> > In most cases the policy will never be changed during grid's lifetime.
> > No need for an explicit call to API on grid start.
> > A joining node should check a local configuration value to match the
> grid.
> > If a dynamic value is already present in a metastore, it should override
> > static value with a warning.
>
> To sum it up:
> - ShutdownPolicy can be set with static configuration
> (IgniteConfiguration#setShutdownPolicy), on join we validate that
> statically configured policies on different server nodes are the same
> - It's possible to override statically configured value by adding
> distributed metastorage value, which can be done by
> calling ignite.cluster().setShutdownPolicy(plc) or control.sh method
> - Dynamic property is persisted
>
> Generally, I don't mind if we have both dynamic and static configuration
> properties. Necessity to call ignite.cluster().setShutdownPolicy(plc); on
> every new cluster creation is a usability issue itself.
> What bothers me here are the possible conflicts between static and dynamic
> configuration. User may be surprised if he has shutdown policy X in
> IgniteConfiguration, but the cluster behaves according to policy Y (because
> several months ago another admin had called
> IgniteCluster#setShutdownPolicy).
> We can handle it by adding a separate enum field to the shutdown policy:
>
> > public enum ShutdownPolicy {
> >   /* Default value of dynamic shutdown policy property. If it's set, the
> > shutdown policy is resolved according to value of static {@link
> > IgniteConfiguration#shutdownPolicy} configuration parameter. */
> >   USE_STATIC_CONFIGURATION,
> >
> >   /* Node leaves the cluster even if it's the last owner of some
> > partitions. Only partitions of caches with backups > 0 are taken into
> > account. */
> >   IMMEDIATE,
> >
> >   /* Shutdown is blocked until node is safe to leave without the data
> > loss. */
> >   GRACEFUL
> > }
> >
> This way:
> 1) User may easily understand whether the static parameter is overridden by
> dynamic. If ignite.cluster().getShutdownPolicy() return anything except
> USE_STATIC_CONFIGURATION, behavior is overridden.
> 2) User may clear previous overriding by calling
> ignite.cluster().setShutdownPolicy(USE_STATIC_CONFIGURATION). After that,
> behavior will be resolved based in IgniteConfiguration#shutdownPolicy
> again.
> If we agree on this mechanism, I propose to use IMMEDIATE name instead of
> DEFAULT for non-safe policy in order to don't confuse user.
> Meanwhile, static configuration will accept the same enum, but
> USE_STATIC_CONFIGURATION will be restricted:
>
> > public class IgniteConfiguration {
> >   public static final ShutdownPolicy DFLT_STATIC_SHUTDOWN_POLICY =
> > IMMEDIATE;
> >   private ShutdownPolicy shutdownPolicy = DFLT_STATIC_SHUTDOWN_POLICY;
> >   ...
> >   public void setShutdownPolicy(ShutdownPolicy shutdownPlc) {
> >     if (shutdownPlc ==  USE_STATIC_CONFIGURATION)
> >       throw new IllegalArgumentException("USE_STATIC_CONFIGURATION can
> > only be passed as dynamic property value via
> > ignite.cluster().setShutdownPolicy");
> >     ...
> >   }
> > ...
> > }
> >
>
> What do you think?
>
> On Tue, Jun 9, 2020 at 3:09 PM Ivan Rakov <ivan.glu...@gmail.com> wrote:
>
> > Alex,
> >
> > Also shutdown policy must be always consistent on the grid or
> unintentional
> >> data loss is possible if two nodes are stopping simultaneously with
> >> different policies.
> >
> >  Totally agree.
> >
> > Let's use shutdownPolicy=DEFAULT|GRACEFUL, as was proposed by me earlier.
> >
> >  I'm ok with GRACEFUL instead of WAIT_FOR_BACKUPS.
> >
> > 5. Let's keep a static property for simplifying setting of initial
> >> behavior.
> >> In most cases the policy will never be changed during grid's lifetime.
> >> No need for an explicit call to API on grid start.
> >> A joining node should check a local configuration value to match the
> grid.
> >> If a dynamic value is already present in a metastore, it should override
> >> static value with a warning.
> >
> > To sum it up:
> > - ShutdownPolicy can be set with static configuration
> > (IgniteConfiguration#setShutdownPolicy), on join we validate that
> > statically configured policies on different server nodes are the same
> > - It's possible to override statically configured value by adding
> > distributed metastorage value, which can be done by
> > calling ignite.cluster().setShutdownPolicy(plc) or control.sh method
> > - Dynamic property is persisted
> >
> > Generally, I don't mind if we have both dynamic and static configuration
> > properties. Necessity to call ignite.cluster().setShutdownPolicy(plc); on
> > every new cluster creation is a usability issue itself.
> > What bothers me here are the possible conflicts between static and
> dynamic
> > configuration. User may be surprised if he has shutdown policy X in
> > IgniteConfiguration, but the cluster behaves according to policy Y
> (because
> > several months ago another admin had called
> > IgniteCluster#setShutdownPolicy).
> > We can handle it by adding a separate enum field to the shutdown policy:
> >
> >> public enum ShutdownPolicy {
> >>   /* Default value of dynamic shutdown policy property. If it's set, the
> >> shutdown policy is resolved according to value of static {@link
> >> IgniteConfiguration#shutdownPolicy} configuration parameter. */
> >>   USE_STATIC_CONFIGURATION,
> >>
> >>   /* Node leaves the cluster even if it's the last owner of some
> >> partitions. Only partitions of caches with backups > 0 are taken into
> >> account. */
> >>   IMMEDIATE,
> >>
> >>   /* Shutdown is blocked until node is safe to leave without the data
> >> loss. */
> >>   GRACEFUL
> >> }
> >>
> > This way:
> > 1) User may easily understand whether the static parameter is overridden
> > by dynamic. If ignite.cluster().getShutdownPolicy() return anything
> except
> > USE_STATIC_CONFIGURATION, behavior is overridden.
> > 2) User may clear previous overriding by calling
> > ignite.cluster().setShutdownPolicy(USE_STATIC_CONFIGURATION). After that,
> > behavior will be resolved based in IgniteConfiguration#shutdownPolicy
> again.
> > If we agree on this mechanism, I propose to use IMMEDIATE name instead of
> > DEFAULT for non-safe policy in order to don't confuse user.
> > Meanwhile, static configuration will accept the same enum, but
> > USE_STATIC_CONFIGURATION will be restricted:
> >
> >> public class IgniteConfiguration {
> >>   public static final ShutdownPolicy DFLT_STATIC_SHUTDOWN_POLICY =
> >> IMMEDIATE;
> >>   private ShutdownPolicy shutdownPolicy = DFLT_STATIC_SHUTDOWN_POLICY;
> >>   ...
> >>   public void setShutdownPolicy(ShutdownPolicy shutdownPlc) {
> >>     if (shutdownPlc ==  USE_STATIC_CONFIGURATION)
> >>       throw new IllegalArgumentException("USE_STATIC_CONFIGURATION can
> >> only be passed as dynamic property value via
> >> ignite.cluster().setShutdownPolicy");
> >>     ...
> >>   }
> >> ...
> >> }
> >>
> >
> > What do you think?
> >
> > On Tue, Jun 9, 2020 at 11:46 AM Alexei Scherbakov <
> > alexey.scherbak...@gmail.com> wrote:
> >
> >> Ivan Rakov,
> >>
> >> Your proposal overall looks good to me. My comments:
> >>
> >> 1. I would avoid adding such a method, because it will be impossible to
> >> change it in the future if some more shutdown policies will be
> introduced
> >> later.
> >> Also shutdown policy must be always consistent on the grid or
> >> unintentional
> >> data loss is possible if two nodes are stopping simultaneously with
> >> different policies.
> >>
> >> This behavior can be achieved by changing policy globally when stopping
> a
> >> node:
> >> ignite.cluster().setShutdownPolicy(DEFAULT);
> >> ignore.stop();
> >>
> >> 2. defaultShutdownPolicy with DEFAULT value is a mess. WAIT_FOR_BACKUPS
> is
> >> not very clear either.
> >> Let's use shutdownPolicy=DEFAULT|GRACEFUL, as was proposed by me
> earlier.
> >>
> >> 3. OK
> >>
> >> 4. OK
> >>
> >> 5. Let's keep a static property for simplifying setting of initial
> >> behavior.
> >> In most cases the policy will never be changed during grid's lifetime.
> >> No need for an explicit call to API on grid start.
> >> A joining node should check a local configuration value to match the
> grid.
> >> If a dynamic value is already present in a metastore, it should override
> >> static value with a warning.
> >>
> >>
> >>
> >>
> >> пн, 8 июн. 2020 г. в 19:06, Ivan Rakov <ivan.glu...@gmail.com>:
> >>
> >> > Vlad, thanks for starting this discussion.
> >> >
> >> > I'll try to clarify the motivation for this change as I see it.
> >> > In general, Ignite clusters are vulnerable to the data loss. Of
> course,
> >> we
> >> > have configurable PartitionLossPolicy, which allows to handle data
> loss
> >> > safely and mitigate its consequences. But being able to avoid critical
> >> > situations is always better than being able to recover from it.
> >> >
> >> > The most common issue from my perspective is absence of a way to
> perform
> >> > rolling cluster restart safely. Scenario:
> >> > 1. Backup count is 1
> >> > 2. Admin wants to perform rolling restart in order to deploy new
> >> version of
> >> > business code that uses Ignite in embedded mode
> >> > 3. Admin shuts down first node, replaces needed binaries and returns
> the
> >> > node back to the topology
> >> > 4. Node joins the cluster successfully
> >> > 5. Admin shuts down second node
> >> > 6. Data loss happens: the second node was the only owner of a certain
> >> > partition, which was being rebalanced from the second node to the
> first
> >> >
> >> > We can prevent such situations by introducing "safe shutdown by
> default"
> >> > mode, which blocks stopping node while it remains the only owner for
> at
> >> > least one partition. It should be applied to "common" ways of stopping
> >> > nodes - Ignite.close() and kill <pid>.
> >> > I think, option to be enabled or disabled in runtime should be a
> >> > requirement for this behavior. Safe shutdown mode has weird
> >> side-effects.
> >> > For example, admin won't be able to stop the whole cluster: stop of
> last
> >> > node will be blocked, because the last node is the only present owner
> of
> >> > all its partitions. Sure, kill -9 will resolve it, but it's still a
> >> > usability issue.
> >> >
> >> > With the described dynamic property scenario will be changed as
> follows:
> >> > 1. Admin enables "safe shutdown" mode
> >> > 2. Admin shuts down first node, replaces needed binaries and returns
> the
> >> > node back to the topology
> >> > 3. Admin shuts down second node (with either ignite.close() or kill
> >> <pid>),
> >> > shutdown is blocked until the first node returns to the topology and
> >> > completes the rebalancing process
> >> > 4. Admin proceeds the rolling restart procedure
> >> > 5. Admin disables "safe shutdown" mode
> >> >
> >> > This logic will also simplify the rolling restart scenario in K8S. Pod
> >> with
> >> > Ignite node won't be terminated until its termination will cause data
> >> loss.
> >> >
> >> > Aside from waiting for backups, Ignition interface provide lots of
> >> options
> >> > to perform various node stop:
> >> > - Whether or not to cancel pending compute jobs
> >> > - Whether or not to perform instant halt() instead of any graceful
> stop
> >> > logic
> >> > - Whether or not to wait for some timeout before halt()
> >> > - Whether or not the stopped grid should be restarted
> >> > All these "stop" methods provide very custom logic. I don't see a need
> >> to
> >> > make them part of dynamic cluster-wide configuration. They still can
> be
> >> > invoked directly via Java API. Later we can extract some of them to
> >> dynamic
> >> > cluster-wide parameters of default stop if it will become necessary.
> >> That's
> >> > why I think we should create an enum for default shutdown policy, but
> >> only
> >> > with two options so far (we can add more later): DEFAULT and
> >> > WAIT_FOR_BACKUPS.
> >> > Regarding the "NORMAL" option that you propose (where the node is not
> >> > stopped until the rebalance is finished): I don't think that we should
> >> add
> >> > it. It doesn't ensure any strict guarantees: the data still can be
> lost
> >> > with it.
> >> >
> >> > To sum it up, I propose:
> >> > 1. Add a new method to Ignition interface to make it possible to stop
> >> with
> >> > "wait for backups" logic directly via Java API, like
> >> Ignition.stop(boolean
> >> > cancel, boolean waitForBackups)
> >> > 2. Introduce "defaultShutdownPolicy" as a dynamic cluster
> configuration,
> >> > two values are available so far: DEFAULT and WAIT_FOR_BACKUPS
> >> > 3. This property is stored in the distributed metastorage (thus
> >> persisted),
> >> > can be changed via Java API and ./control.sh
> >> > 4. Behavior configured with this property will be applied only on
> common
> >> > ways of stopping the node - Ignite.close() and kill <pid>.
> >> > 5. *Don't* add new options to the static IgniteConfiguration to avoid
> >> > conflicts between dynamic and static configuration
> >> >
> >> > --
> >> > Best Regards,
> >> > Ivan Rakov
> >> >
> >> > On Mon, Jun 8, 2020 at 6:44 PM V.Pyatkov <vldpyat...@gmail.com>
> wrote:
> >> >
> >> > > Hi
> >> > >
> >> > > We need to have ability to calling shutdown with various guaranties.
> >> > > For example:
> >> > > Need to reboot a node, but after that node should be available for
> >> > > historical rebalance (all partitions in MOVING state should have
> gone
> >> to
> >> > > OWNING).
> >> > >
> >> > > Implemented a circled reboot of cluster, but all data should be
> >> available
> >> > > on
> >> > > that time (at least one copy of partition should be available in
> >> > cluster).
> >> > >
> >> > > Need to wait not only data available, but all jobs (before this
> >> behavior
> >> > > available through a stop(false) method invocation).
> >> > >
> >> > > All these reason required various behavior before shutting down
> node.
> >> > > I propose slightly modify public API and add here method which shown
> >> on
> >> > > shutdown behavior directly:
> >> > > Ignite.close(Shutdown)
> >> > >
> >> > > /public enum Shutdownn {
> >> > >     /**
> >> > >      * Stop immediately as soon components are ready.
> >> > >      */
> >> > >     IMMEDIATE,
> >> > >     /**
> >> > >      * Stop node when all partitions completed moving from/to this
> >> node
> >> > to
> >> > > another.
> >> > >      */
> >> > >     NORMAL,
> >> > >     /**
> >> > >      * Node will stop if and only if it does not store any unique
> >> > > partitions, that does not have copies on cluster.
> >> > >      */
> >> > >     GRACEFUL,
> >> > >     /**
> >> > >      * Node stops graceful and wait all jobs before shutdown.
> >> > >      */
> >> > >     ALL
> >> > > }/
> >> > >
> >> > > Method close without parameter Ignite.close() will get shutdown
> >> behavior
> >> > > configured for cluster wide. It will be implemented through
> >> distributed
> >> > > meta
> >> > > storage and additional utilities for configuration.
> >> > > Also, will be added a method to configure shutdown on start, this is
> >> look
> >> > > as
> >> > > IgniteConfiguration.setShutdown(Shutdown).
> >> > > If shutting down did not configure all be worked as before according
> >> to
> >> > > IMMEDIATE behavior.
> >> > > All other close method will be marked as deprecated.
> >> > >
> >> > > I will be waiting for your opinions.
> >> > >
> >> > >
> >> > >
> >> > > --
> >> > > Sent from: http://apache-ignite-developers.2346864.n4.nabble.com/
> >> > >
> >> >
> >>
> >>
> >> --
> >>
> >> Best regards,
> >> Alexei Scherbakov
> >>
> >
>


-- 

Best regards,
Alexei Scherbakov