On Sat, Oct 4, 2008 at 8:44 AM, Arnaud Quette <[EMAIL PROTECTED]> wrote:
> 2008/10/4 Raphael Geissert <[EMAIL PROTECTED]>:
>> Package: nut
>> Version: 2.2.2-8
>> Severity: wishlist
>> Tags: patch
[...]
>> * the battery charge information, at least as displayed by knutclient 0.9.4,
>> is either 0% or 100%, the latter only being displayed when the UPS is fully
>> charged.
>> * the runtime info is only updated after a test.battery.start.<quick/deep>,
>> there's no calibrate.<start/stop> for it.
>
> I don't know much about TL devices, and I've not dug the ml, but
> Charles might have an answer to that.

I don't know much about the Tripp Lite devices covered by the
usbhid-ups driver, but the usual debug suggestions apply. You can run
the driver with -DDD on the command line, and look for messages
related to battery charge.

Going out on a limb here, maybe it's something that we have to
explicitly poll (versus waiting for it to be reported on the interrupt
pipe), for the times when it is below 100%.

In any case, it's probably a good idea to first verify that knutclient
agrees with upsc.

-- 
- Charles Lepple



-- 
To UNSUBSCRIBE, email to [EMAIL PROTECTED]
with a subject of "unsubscribe". Trouble? Contact [EMAIL PROTECTED]

Reply via email to