andvasp commented on code in PR #2673:
URL: https://github.com/apache/plc4x/pull/2673#discussion_r3731015711


##########
plc4j/drivers/eip/src/main/java/org/apache/plc4x/java/eip/base/EipTcpConnection.java:
##########
@@ -767,12 +765,7 @@ private static byte[] toAnsi(String tag) throws 
BufferException {
             segments.add(newSegment);
             lengthBytes += newSegment.getLengthInBytes();
         }
-        WriteBufferByteBased buffer = new WriteBufferByteBased(new 
byte[lengthBytes],
-            WithByteBasedOption.WithByteOrder("LITTLE_ENDIAN"),
-            WithOption.WithUnsignedIntegerEncoding("unsigned-binary"),
-            WithOption.WithSignedIntegerEncoding("twos-complement"),
-            WithOption.WithFloatEncoding("IEEE754"),

Review Comment:
   > I'm a bit surprized this would work ... if I look in mspec, the type 
PathSegment doesn't define the different encodings. So they should be null if 
you remove them all. It should require setting the unsigned integer and the 
string encodings. Also would you be changing the endianess from little-endian 
to big-endian.
   
   Now that you mentioned the point about byte order, I am surprised too why it 
was working because it looks like it is mixing the byte order. Let me summarise 
my scenario:
   
   - I did not change the configuration of the byte order. So I am using big 
endian.
   - I can read the value of most of the tags.
   - There are some tags that I cannot, even on same device (addressing this 
issue later) but I did not check them after the modification of this PR.
   - I did not have the opportunity to test the write value but I can and I 
plan to do.
   



-- 