We have a couple of the dualfuel generators. I really like them. We've only ever used them with propane. Small enough to carry around, and will run for over a day on a 30lb tank (with our normal site load), and we're somewhat suburban, so within 30 minutes I can get to a store that does propane tank exchanges. The thing I don't like about them is there is no 'weather proofing' on them. The outlets are just exposed on the side, along with all the control switches. Maybe they're all sealed, but nothing says that. I'm always worried about deploying them in a rain storm. All the promo pieces show people using them on their picnics and RV's on bright sunny summer days. Years ago, I had one of my gas generators fail during a sunny afternoon power outage. At a landscaper, the tree sprinklers decided to turn on, and shorted out the generator, so I think that heavy rain might do the same thing. Some simple weatherproofing would have prevented that, but I haven't seen any small portable generators that have that.

On 1/31/2020 9:28 AM, ch...@wbmfg.com wrote:
The problems I have with diesels are as follow:
The fuel goes stale. You can treat it but it still has problems with age. Most of us want a large tank, but with just short weekly exercise cycles that fuel might be in the tank for years. The fuel poses a hazardous clean up risk. Both with refueling and with a fuel line break. Huge problem if you are in a national forest or really any public land. Fuels can gel and make the generator not start in zero and below zero conditions. Also diesels are just notoriously hard to start when cold. All liquid cooled generators I have ever seen have block heaters, but Murphy says that block heaters and engine start batteries will always fail prior to actually needing the generator. I think I have had more trouble with the trickle chargers for the engine start batts than anything else. That is why I remote the battery inside to a heated area and put a better charger on it than comes with the generator.
But you can refuel them yourself.
There are tri fuel generator carburetors that will take gasoline, natural gas and propane. To me that is the ultimate in redundant backups.
*From:* Nate Burke
*Sent:* Friday, January 31, 2020 8:14 AM
*To:* AnimalFarm Microwave Users Group
*Subject:* Re: [AFMUG] Generator advice..
What brand Diesel generator are you using? Are they permanent or portable?

On 1/31/2020 2:51 AM, Mike Meluskey wrote:

In the islands we get lots of power outages.
Our go-to generator for a site like you described is a 12.5kw diesel generator.
Diesel is much easier to re-fuel after a disaster (ie. Cat5 Hurricane).
I became an expert at re-fueling, oil changes, priming, clogged fuel filters, etc. after Hurricane Maria. People with propane/natural gas generators could not get them re-filled easily during our 2 - 3 months with no Utility power. Generac’s did not hold up well, lots of fried circuit boards.

Again, this was on a small island in the Caribbean. Generac natural gas generators might be a good fit for your environment.

On 30 Jan 2020, at 18:59, Nate Burke wrote:

    We've seen that too, running an (industrial) 120v garage door
    opener, pulled one leg out of phase/voltage enough with the
    starting current that the control board shutdown the generator
    (15kw diesel).   It ran a 5ton 240v AC unit cycling on and off
    just fine.

    On 1/30/2020 4:49 PM, Adam Moffett wrote:

    Using 240V AC may help with that.

    We had trouble where the generator had way more load on one hot
    leg than the other.  It ran rough and stalled often.

    On 1/30/2020 5:14 PM, Chuck McCown wrote:
    The only reason you might have trouble is the air conditioning
    starting load.  I have seen them cause a generator to stall and
    die before.

    Sent from my iPhone

    On Jan 30, 2020, at 2:16 PM, Josh Baird
    mailto:joshba...@gmail.com wrote:

    
We're shopping for a generator for one of our larger POP's. The electrical contractor is recommending this:
    
https://www.generac.com/all-products/generators/home-backup-generators/guardian-series/22kw-7043-whole-house-switch-wifi-enabled
    This would be supporting 4 30A circuits (powering 4 APC UPS)
    that are currently drawing about 30A between them (powering
    network gear and servers).  There is also one of the on-wall
    indoor/outdoor air conditioners in this room - unsure what
    it's drawing.
    The contractor also seems to think that this generator, with a
    second transfer switch can power the remainder of the small
    building which includes some lighting, a refrigerator and some
    small electronics like PC's, etc.
    Can someone who actually knows something about generators and
    this kind of stuff give me some advice here?  Will this
    generator support our load and not fall over?
    Thanks!
-- AF mailing list
    AF@af.afmug.com
    http://af.afmug.com/mailman/listinfo/af_af.afmug.com




-- AF mailing list
    AF@af.afmug.com
    http://af.afmug.com/mailman/listinfo/af_af.afmug.com




------------------------------------------------------------------------
--
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com



-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to